I understand it is not really modicon modbus but can be beaten to work. Does anyone have any tips?
Thanks Robert |
|
|
|
|
|
|
|
|
Hello,
The Siemens S7-1200 would need to talk Modbus RTU via an RS-485 connection in order to poll data from the base radio. Thanks ------------------------- Martin Chartrand Application and Sales Support Specialist Control Microsystems Inc. mchartrand@controlmicrosystems.com www.controlmicrosystems.com Tel: (613) 591-3878 Ext.254 Fax: (613) 591-3145 |
|
|
|
|
|
|
|
|
Right. I am hoping someone can advise of bit and word order as well as any offset used and if they use the 4 in 40k registers or not.
|
|
|
|
|
|
|
|
|
There are two possible addressing modes. You need to refer to the user manual for the correct Modbus register addresses for whichever mode you select. The user manual can be found here:
http://www.accutechinstruments...ch-software-download/ You will need to download and install Accutech Manager (free of charge) in order to get to the .chm user manual. Thanks. ------------------------- Martin Chartrand Application and Sales Support Specialist Control Microsystems Inc. mchartrand@controlmicrosystems.com www.controlmicrosystems.com Tel: (613) 591-3878 Ext.254 Fax: (613) 591-3145 |
|
|
|
|
|
|
|
|
I hear that base radio firmware 1.86 will have word order selections supporting 1234, 3412, 2143 and 4321 which will make most these type integration issues go away.
4321 is used by Thermo AutoPilot legacy versions where comm parameters are not selectable. These selections are made from the pushbuttons on the base radio. |
|
|
|
|
|
|
|
|
I've been advised by our Software engineers that this is correct.
Regards ------------------------- Martin Chartrand Application and Sales Support Specialist Control Microsystems Inc. mchartrand@controlmicrosystems.com www.controlmicrosystems.com Tel: (613) 591-3878 Ext.254 Fax: (613) 591-3145 |
|
|
|
|
FuseTalk Standard Edition v3.2 - © 1999-2010 FuseTalk Inc. All rights reserved.
Copyright © 2010 Control Microsystems Inc. All rights reserved. This forum is provided as an environment in which users of Control Microsystems hardware and software products may share information regarding the use and application of these products. Although Control Microsystems employees do interact with users on this forum, a response to every message posting is not guaranteed. If you need immediate technical support, please contact our Technical Support Department at the coordinates found on the following link: http://controlmicrosystems.com/contact-us/support/.